مشاهدة النسخة كاملة : الماء المستخدم في الخلطات الخرسانية


شكرية
10-25-2007, 08:11 AM
هل يمكن استخدام مياه الابار الارتوازية في الخلطات الخرسانية

alhanini
10-28-2007, 06:23 PM
المياه عادة أن كانت صالحة للشرب فهي صالحة للخلطات الخرسانية هذا مبدأ بسيط يمكن أن يفيدك في هذا الموقف .

شكرية
11-27-2007, 07:52 AM
شكرا على الرد يا زميلي العزيز

sHeBoOo
11-28-2007, 09:27 PM
Mixing Water for Concrete


The requirements of mixing water for concrete


Almost any natural water that is drinkable and has no pronounced taste or odor can be used as mixing water for making concrete.

Drinkable Water is good for making concrete

• Some waters that are not fit for drinking may be suitable for concrete making provided that they satisfy the acceptance criteria laid by ASTM C 94 (Tables 3.1)


Table 3.1 Acceptance Criteria for Questionable Water Supplies (ASTM C 94)

Limits Test method
Compressive Strength, minimum percentage of control at 7 days 90 ASTM C 109 or T 106
Time of set, deviation from control, hr:min From 1:00 earlier to 1:30 later ASTM C 191 or T 131










Effects of Impurities in Mixing Water

Excessive impurities in mixing water affect setting time and concrete strength and also cause efflorescence (deposits of white salts on the surface of concrete), staining, corrosion of reinforcement, volume changes, and reduced durability

Impurity Effects
1. Alkali carbonate and bicarbonate Acceleration or retardation of setting time. Reduction in strength
2. Chloride Corrosion of steel in concrete
3. Sulfate Expansive reactions and deterioration of concrete. Mild effect on corrosion of steel in concrete
4. Iron salts Reduction in strength
5. Miscellaneous inorganic salts (zinc, copper, lead, etc) Reduction in strength and large variations in setting time
6. Organic substances Reduction in strength and large variations in setting time
7. Sugar Severely retards the setting of cement
8. Silt or suspended particles Reduction in strength
9. Oils Reduction in strength


Use of Questionable Waters as Mixing Water

Sea Water

• Seawater containing up to 35,000 ppm of dissolved salts is generally suitable as mixing water for plain concrete

• Seawater is not suitable for use in making steel reinforced concrete and prestressed concrete due to high risk of steel corrosion


Acid Waters

• Acid waters may be accepted as mixing water on the basis of their pH values.
• Use of acid waters with pH values less than 3.0 should be avoided.
• Organic acids, such as tannic acid can have significant effect on strength at higher concentrations.



Alkaline Waters

• Waters with sodium hydroxide concentrations up to 0.5 % and potassium hydroxide in concentrations up to 1.2 % by weight of cement has no significant effect on strength.

• The possibility for increased alkali-aggregate reactivity should be considered before using the alkaline water as mixing water.
• Tannic acid can have significant effect on strength at higher concentrations.

Wash Waters
• Wash waters may be reused as mixing water in concrete if they satisfy the limits in Tables 3.2

Table 3.2 Chemical Limits for Wash Water used as Mixing water (ASTM C 94)

Chemical or type of construction Maximum concentration, ppm Test Method
Chloride, as Cl ASTM D 512
Prestressed concrete or concrete in bridge decks 500
Other reinforced concrete 1000
Sulfate, SO4 3,000 ASTM D 516
Alkalies, as (Na2O+0.658 K2O) 600
Total solids 50,000 AASHTO T 26


Industrial Wastewaters

• Industrial wastewaters may be used as mixing water in concrete as long as they only cause a very small reduction in compressive strength, generally not greater than 10 % to 15 %.
• Wastewaters from paint factories, coke plants, and chemical and galvanizing plants may contain harmful impurities. Thus such wastewaters should not be used as mixing water without testing.

Sanitary Sewage

• The sanitary sewage may be safely used as mixing water after treatment or dilution of the organic matter.